We have a 40' X24' high geodesic dome which will accommodate an aquaponic system . obviously we will have several pumps running, maybe 10 to fifteen plus a large exhaust fan or two. also some grow lights from time to time. Can anybody tell me what size wiring I should use to run the 125 ft to the dome? . Allowing for some overkill?
Two swamp coolers 15 amps
Lights 30 amps
Pumps 7 amps
Other 7 amps
Draw 30 amps per phase x%125 for being continuous loads =40 amps
Go with #6 copper if in pipe or #4 if direct burry. Feed from 50 amp breaker. Buy large panel with extra space. I would run 1-1/2" underground pipe. Run extra 3/4" pipe for data. Run pipe for water and gas